bdn2004
Electrical
- Jan 27, 2007
- 794
A new rectifier system is installed on an existing unit substation as the simplified sketch shows below. The 45A thermal magnetic circuit breakers that feed the small rectifiers trip shortly after the system is powered up. They heat up to 150 degrees F per infrared testing. We measured the THD at the Mains as shown. The results show a total harmonic distortions at the connection point is 1% Voltage and 18% current.
The manufacturer of the rectifier equipment is claiming the 45A circuit breakers are tripping due to "dirty" input power and of no fault of their own. Note there are fairly large VFDS installed and HVAC equipment off the same substation bus. There are other small loads in the HVAC equipment that have operated for years without tripping. Is the manufacturer right ? Are there other things that could be causing this that we should check for?
The manufacturer of the rectifier equipment is claiming the 45A circuit breakers are tripping due to "dirty" input power and of no fault of their own. Note there are fairly large VFDS installed and HVAC equipment off the same substation bus. There are other small loads in the HVAC equipment that have operated for years without tripping. Is the manufacturer right ? Are there other things that could be causing this that we should check for?