I don't know if I'm over thinking this, so I thought I would reach out.
I'm doing the HAZOP for a new plant we're constructing. The other engineers have installed valves before a pressure transmitter and a conservation vent. They want to take credit in the HAZOP for the high pressure interlock on the transmitters and for the vacuum relief on the conservation vent, but I didn't think we could because there is a manual valve before both of them.
Can we take credit for these even with a manual valve in the line? Would it be okay if we said that the valve is locked open?
I'm doing the HAZOP for a new plant we're constructing. The other engineers have installed valves before a pressure transmitter and a conservation vent. They want to take credit in the HAZOP for the high pressure interlock on the transmitters and for the vacuum relief on the conservation vent, but I didn't think we could because there is a manual valve before both of them.
Can we take credit for these even with a manual valve in the line? Would it be okay if we said that the valve is locked open?