Brad-X
Electrical
- Sep 27, 2017
- 11
I understand from both relevant IEEE standards and in my case the Canadian Electrical Code that services should typically have a grounding electrode for the main service switchboard which is distinct from the ground grid on the main transformer secondary. What I don't fully understand, however, is the purpose of keeping these grids separate. Typically in the smaller commercial/industrial facilities I'm in, the service transformer and main service switchboard are quite close (<25' apart).
Furthermore, I've seen several installations where the switchboard uses the close-by transformer ground grid as it's own grounding electrode via the neutral. Can someone explain the danger of this kind of setup?
For Context:
-I'm typically dealing with primary voltages of 27.6kV and under, and secondary voltage of 600/347V.
-Service transformers are either grounded wye-grounded wye or delta-grounded wye.
Furthermore, I've seen several installations where the switchboard uses the close-by transformer ground grid as it's own grounding electrode via the neutral. Can someone explain the danger of this kind of setup?
For Context:
-I'm typically dealing with primary voltages of 27.6kV and under, and secondary voltage of 600/347V.
-Service transformers are either grounded wye-grounded wye or delta-grounded wye.