msm15
Mechanical
- Apr 22, 2010
- 18
I guess my real question is can someone please explain to me what the difference is between "Allowable flow - gpm" and "Theoretical discharge"
I have to admit my experience is a little limited in this area so I am just going based off what I read and charts I found, but the reason I ask is because we have to bring in a new water main into a building for domestic service. We will only be supplying water to a few bathrooms - a total of 2 urinals, 8 toilets, and 5 sinks. I get a total of about 33 fixture units for a demand of about 40 gpm. The building is set back about 160' off the street so we will have to run a decent amount of pipe but I know the street pressure is about 50 psi at 500 gpm residual as measured off the nearest hydrant.
Based on those #'s I get a theoretical discharge of 844 gpm on a 2" pipe @50 psi (NFPA 24 Table c.4.10.1(a). We want to use an 1-1/2" - with a theoretical discharge of 474 gpm
DEP has on file that the "Allowable Flow" for a 2" starts at 100 gpm and goes down as the pipe gets longer. I cant say I have ever seen anyone sitting there regulating the gpm's on these pipes and I know the flow out of the hydrant orifice is a lot more then the "Allowable Flow" so what am I missing - why cant we size the pipe based on theoretical discharge
I have to admit my experience is a little limited in this area so I am just going based off what I read and charts I found, but the reason I ask is because we have to bring in a new water main into a building for domestic service. We will only be supplying water to a few bathrooms - a total of 2 urinals, 8 toilets, and 5 sinks. I get a total of about 33 fixture units for a demand of about 40 gpm. The building is set back about 160' off the street so we will have to run a decent amount of pipe but I know the street pressure is about 50 psi at 500 gpm residual as measured off the nearest hydrant.
Based on those #'s I get a theoretical discharge of 844 gpm on a 2" pipe @50 psi (NFPA 24 Table c.4.10.1(a). We want to use an 1-1/2" - with a theoretical discharge of 474 gpm
DEP has on file that the "Allowable Flow" for a 2" starts at 100 gpm and goes down as the pipe gets longer. I cant say I have ever seen anyone sitting there regulating the gpm's on these pipes and I know the flow out of the hydrant orifice is a lot more then the "Allowable Flow" so what am I missing - why cant we size the pipe based on theoretical discharge