Hello,
Quick question on which set of deflection limits apply in certain situations. This isn't a structural issue, but it is a serviceability issue.
I have a house where a 2'-0" cantilever (21'-0" span) was built by extending 2 parallel beams (21'-0" apart) over the cant and then installing joists between the beams. Not how I would have designed it, but hey - can't win them all.
As you would expect, the home owner is noticing a 'hump' because the floor joist right at the start of the cant sits on the bearing wall below it, and the 21' long LVL at the end of the cantilever is deflecting ~ 1/2".
No, I've contacted the designer and he is defending it as the two beams supporting the cantilevers are only deflecting 0.04" (less than L/90) and the joist between the beam is deflecting .35" (combined for less than L/360)
My argument is the beam spanning the length of the cant also has to abide by the L/90 deflection limit as it is (logically speaking) a part of the cantilever as a whole, and doesn't meet the L/90 requirement at mid span.
Sketch to make up my terrible explanation: [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1431021065/tips/SBizHubC22-15050623510_crpenr.pdf[/url]
Quick question on which set of deflection limits apply in certain situations. This isn't a structural issue, but it is a serviceability issue.
I have a house where a 2'-0" cantilever (21'-0" span) was built by extending 2 parallel beams (21'-0" apart) over the cant and then installing joists between the beams. Not how I would have designed it, but hey - can't win them all.
As you would expect, the home owner is noticing a 'hump' because the floor joist right at the start of the cant sits on the bearing wall below it, and the 21' long LVL at the end of the cantilever is deflecting ~ 1/2".
No, I've contacted the designer and he is defending it as the two beams supporting the cantilevers are only deflecting 0.04" (less than L/90) and the joist between the beam is deflecting .35" (combined for less than L/360)
My argument is the beam spanning the length of the cant also has to abide by the L/90 deflection limit as it is (logically speaking) a part of the cantilever as a whole, and doesn't meet the L/90 requirement at mid span.
Sketch to make up my terrible explanation: [URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1431021065/tips/SBizHubC22-15050623510_crpenr.pdf[/url]