Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

cantilever slab

Status
Not open for further replies.

Jandra11

Structural
Jun 18, 2017
109
0
0
PH
we have a project that has a cantilevered slab(1000mm overhang- balcony) on the 3rd floor but due to some circumstances, the concrete on the cantilevered portion is not poured on the same time with the main floor slab. Heres my questions, is it safe to consider it a fully rigid even though it is not monolithic as long as we provide an adequate number of dowels? and what is the consequence of having this kind of cantilevered slab? considering the slab to be PT SLAB
 
Replies continue below

Recommended for you

We would usually allow construction joints at points of maximum moment and try to avoid joints at points of maximum shear.
In your case, is the joint at a high shear condition? Or is the joint over a supporting member where shear isn't an issue?

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Status
Not open for further replies.
Back
Top