I was provided the attached figure considering for single story, lightly loaded (SDC A, 115mph wind) wood frame office building. My initial concern is uneven bearing stiffness between the concrete and insulation would lead to cantilever or cross grain bending in the sill?
This is similar to Figure 1 in the attached article I think pulled the picture from.
Let's say the minimum "stem" width of 3-1/2" to allow for a screw anchor, and would fit a washer. This would be a 2" "overhang" for the sill plate. Since the bearing stiffness is non-uniform below the sill plate, there should be a nonzero amount of bending in the sill?
Another issue appears to be if shear loads in the wall exceed 400 plf, I'd need the washer to be within 1/2" of the loaded side. This seems to then be the far side of the wall. So custom cut washers?
Anyone else seen a detail such as this? Any thoughts from field install?
Thanks in advance
This is similar to Figure 1 in the attached article I think pulled the picture from.
Let's say the minimum "stem" width of 3-1/2" to allow for a screw anchor, and would fit a washer. This would be a 2" "overhang" for the sill plate. Since the bearing stiffness is non-uniform below the sill plate, there should be a nonzero amount of bending in the sill?
Another issue appears to be if shear loads in the wall exceed 400 plf, I'd need the washer to be within 1/2" of the loaded side. This seems to then be the far side of the wall. So custom cut washers?
Anyone else seen a detail such as this? Any thoughts from field install?