buzzp
Electrical
- Nov 21, 2001
- 2,032
We have a 100kV/21.6kV substation. On the secondary side we have 4 cap banks, 300kVAR each, setup in a delta. We then go through 13000 ft of 636 to another cap bank (3 banks at 900kVAR each). After another 2500 ft of 636, we go to a 21.6kV/4160V transformer, which has a cap bank of 600kVAR and it is on the 4160V side. All cap banks have current limiting reactors. Please see the two attached drawings. Yes I know this is not typical to have this many banks.
When we have a fault that shuts down the (6) 4000VAC motors (total 8850HP), we will often times blow a fuse or fuses in 'cap bank 1' near the substation. On occasion, the reactors will also come apart.
One of my concerns is the delta configuration of the cap bank by the substation. It seems this configuration will provide for the highest currents when we trip the 8850HP due to the cable inductance. We don't blow fuses or trip breakers on Cap bank 2 or 3 but they are much closer to the 8850HP load. Will changing this bank to a Y help us out to give the current some place to go rather than recirculating around the cap bank?
What other solutions should I be looking at such as surge arrestors, etc.?
When we have a fault that shuts down the (6) 4000VAC motors (total 8850HP), we will often times blow a fuse or fuses in 'cap bank 1' near the substation. On occasion, the reactors will also come apart.
One of my concerns is the delta configuration of the cap bank by the substation. It seems this configuration will provide for the highest currents when we trip the 8850HP due to the cable inductance. We don't blow fuses or trip breakers on Cap bank 2 or 3 but they are much closer to the 8850HP load. Will changing this bank to a Y help us out to give the current some place to go rather than recirculating around the cap bank?
What other solutions should I be looking at such as surge arrestors, etc.?