JTS
Industrial
- Jun 22, 2015
- 8
We are designing a power distribution system,12.47kV and 480V,and we are spec'ing an S&C Vista switch for the MV side. It has become our standard that for arc-flash mitigation on the 12.47kV-480V transformer secondary conductors bushing CT's be installed on the low side bushings of the transformer itself. The CT secondaries then run into a relay which is located in the PDC, and a trip circuit is ran from the relay back up to the MV OCPD feeding the transformer. The trip circuit is wetted from a CPT on the line side of the PDC main. In the instance that an event will cause an undervoltage scenario on the CPT a capacitive trip device (CTD) is installed to ensure that the trip circuit maintains its wetting voltage. The problem is that the standard CTD output is 170VDC due to the peak AC input and S&C says that it's maximum external trip is 125VDC. This leaves us with two options.
1. Use the CTD anyway and make sure that a B contact is in line with the trip circuit to ensure that the signal is momentary, and in the event of a trip check all contacts and ensure there has been no damage.
2. Forgo the CTD altogether and use a Voltage Sag Corrector with a 200ms ride through on full voltage loss.
I am leaning towards using the Voltage Sag Corrector however I haven't really seen this done anywhere else, is this a typical setup that you have seen and/or spec'd?
1. Use the CTD anyway and make sure that a B contact is in line with the trip circuit to ensure that the signal is momentary, and in the event of a trip check all contacts and ensure there has been no damage.
2. Forgo the CTD altogether and use a Voltage Sag Corrector with a 200ms ride through on full voltage loss.
I am leaning towards using the Voltage Sag Corrector however I haven't really seen this done anywhere else, is this a typical setup that you have seen and/or spec'd?