This is a ungrounded neutral capacitor bank tied to a 34.5kV main power transformer Y grounded. All the A phase fuses blew, not sure why currently. I'm looking at the event and the neutral voltage before the event was 1.2 kV < -178, likely due to voltage imbalance. After the event, before it tripped the neutral voltage as 2.7kV < -157.
From looking at the event phasors the angle should be be nearer to <180 and the voltage would be about 1/3 phase voltage to ground or 6.5kV. (the angle along the line of IA and IB, the voltage magnitude on a line between Vb and Vc)
The voltage was always balanced (20.2/20.5/20.5 kV), the current before the trip was 129.3/143.8/143.7 amps(14.5 amps lower on A phase which blew fuses). Post fault the current was 0/127.7/128.2 amps
Why is the neutral voltage only 2.7kV?
Neutral voltage is VAZ
The synchro-wave oscillography is attached in adobe.
From looking at the event phasors the angle should be be nearer to <180 and the voltage would be about 1/3 phase voltage to ground or 6.5kV. (the angle along the line of IA and IB, the voltage magnitude on a line between Vb and Vc)
The voltage was always balanced (20.2/20.5/20.5 kV), the current before the trip was 129.3/143.8/143.7 amps(14.5 amps lower on A phase which blew fuses). Post fault the current was 0/127.7/128.2 amps
Why is the neutral voltage only 2.7kV?
Neutral voltage is VAZ
The synchro-wave oscillography is attached in adobe.