115kV/13.8kV substation with two 22mVA self tapping xfmrs, four 800amp circuit breakers
feeding four 13.8kV wye distribution circuits, with 477mcm al conductors. Total peak load of
system is 13mW. The system has 7 capacitor banks, of various kVAR ratings, on time control.
System PF is .98 to .99.
Question:
Some large customers are having PF problems (ie .72) within their facilities. If we, as the utility,
correct their PF with a primary installed capacitor bank, will that throw off our system PF which
is indicated back at the sub? These customers are 1.3 miles from the sub.
Also, what is a “good rule of thumb” for locating capacitor banks within a system when you have
concluded the need for them?
Thanks