Capacitor Reforming, why it's needed? 3

Status
Not open for further replies.

gsjhand

Electrical
Jul 17, 2007
34
Can anybody give me an Idea that why capacitor reforming is needed in the cases where a drive has been sitting on shelf for too long? I want to know what changes in capacitor if it's not been used for a long time? Is this required only for the capacitors which are connected to power circuit or is it needed for all the capacitors including the ones which are on control circuit boards?
 
Replies continue below

Recommended for you

Reforming is mostly (only, I would say) used for DC link capacitors in frequency inverters. I have seen an inverter where a rather big capacitor exploded when the inverter was started without reforming the capacitors. Loud bang, lots of aluminum foil all over the place and a big dent in the panel's door.

If the manufacturer says it shall be done - then do it.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Dayymn. Does this apply to power factor capacitors too ? In my rewind shop, I have over 500 KVAR pf correction capacitors which lie unpowered for days together and are used only during motor testing. Of course, when they are used, the voltage is applied gradually through a variac (to reduce motor inrush current) but typical time to reach full voltage level could be as low as a minute. Should I take more time in "reforming" these caps ?



Muthu
 
No edison. It only applies to electrolytic capacitors. All AC capacitors are either paper or film type. So no need to worry.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Typically it is with VFD's where the unit has been unpowered for 2 years or so. A gentle introduction to the electrical world via a variable voltage is advised, for a few hours or so before applying full voltage.
 