We encountered a problem on sylinder tests when we switched testing laboratory. The 1st lab uses sulfur capping on samples; we get results way above the designed strength. The 2nd lab only uses rubber capping and we get results way below the designed strength. We suspect the rubber capping causes eccentricity in load application thus samples easily breaks. Comp machine of lab 1 have expired calib record while that of lab 2 have been calibrated recently. But we dont't expect too big difference in results just because of difference in calibration frequency. Any thoughts on this?