Cascade controller set-point units 1

Status
Not open for further replies.

sysengineer

Electrical
Feb 16, 2012
56
When a controller accepts a remote set-point in cascade mode from another (primary) controller does the output of the primary controller have to be scaled into the engineering units of the secondary measured value (MV)?
 
Replies continue below

Recommended for you

Yes.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
As Xnuke says: Yes.

But, I've worked on some DCS Systems that don't allow changing the Output Engineering Units of the Primary Controller - they were always 0 - 100% and could not be changed to match the engineering units of the secondary controller (like degC). It's very frustrating.....

______________________________________________________________________________
This is normally the space where people post something insightful.
 
input the controller output signal into a math block, scale it, use the math block output
 
Thanks controlnovice. On the DCS systems that don't support changing of engineering units is it just assumed that 0 to 100% output of the primary controller represents 0 to 100% of the the secondary controller measured variable? I.e. if the secondary controller measured variable is 0 to 50 litres/min then the remote setpoint is also a 0 to 50 litres/min signal?
 
Yes:

0-100% of the Master controller output represents the full range of the Secondary controller PV...in your example 0 - 50 lpm.

Keep in mind that typically the Setpoint range of the secondary controller matches the PV Range...so your SP Range would also be 0 - 50 lpm.

If you limit your setpoint maximum to, for example 40 lpm, the 100% output still represents the 50 lpm but the secondary controller won't go above 40.