lfg2007
Mechanical
- Oct 15, 2007
- 17
I have 4 Carrier Centrifigal chillers under commissioning phase. Recently the units (4) shut down while starting on "VFD over temp" alarm. I was told this was caused by the condenser water being warmer than the chilled water. This situation was caused by running the secondary loop without the chillers operating. This was solved by adjusting the condenser bypass valve by the Carrier tech. Question 1) How does modulating the condenser valve help the situation. 2) Should the head pressure control valve be modualted by the unit?