In regards to thread407-167783.
I too have not seen anything in writing about variable speed and the minimum flow requirement for pumps; however, the "standard" practice I have seen in the field is to take the same percentage of the new BEP at the reduced speed.
For example if the pump company states 10% of nominal flow for their minimum. Look at the performance curve at lowest speed you will operate in the application and take 10% of that reduced speed curve's BEP.
As flow is linearly related to speed this is simply the percentage of speed times rate minimum flow. So if standard min. flow is 10GPM then at 80% speed you could consider the minimum flow to be 8GPM. Most variable speed pumps I have seen that come from the factory with drive installed still use the rated minimum flow of the pump. But the mfr will always lean conservative.
Please also keep in mind this is all assuming cool clean water. If this is a boiler feed application with high temp water then your minimum flow will be higher to begin with.
I too have not seen anything in writing about variable speed and the minimum flow requirement for pumps; however, the "standard" practice I have seen in the field is to take the same percentage of the new BEP at the reduced speed.
For example if the pump company states 10% of nominal flow for their minimum. Look at the performance curve at lowest speed you will operate in the application and take 10% of that reduced speed curve's BEP.
As flow is linearly related to speed this is simply the percentage of speed times rate minimum flow. So if standard min. flow is 10GPM then at 80% speed you could consider the minimum flow to be 8GPM. Most variable speed pumps I have seen that come from the factory with drive installed still use the rated minimum flow of the pump. But the mfr will always lean conservative.
Please also keep in mind this is all assuming cool clean water. If this is a boiler feed application with high temp water then your minimum flow will be higher to begin with.