I need change condenser in wall cabinet (with capillary tube as metering device).Old condenser was consisting of 5 circuits. New condenser consist of 3 circuits.
Another parameters of condensers are equal. When I charged by R22 and run system the compressor was flooded. Why?
What should I do for correct working of system?
Thank for any advice.
 
Replies continue below

Recommended for you

I think you might be talking about the evaporator not the condenser.
Capillary systems are critical charge systems. That means the charge must be measured very carefully.
Your cap tube quantity and loading has obviously changed or you did not size them correctly in the first place.
Suggest that you review the system and focus on cap tube sizing.

Good Luck