Changing the rated voltage of a VFD driven motor 2

Status
Not open for further replies.

edison123

Electrical
Oct 23, 2002
4,476
A 220 V, 150 HP, 50 Hz, 375 RPM motor is being driven by a 440 V VFD. The motor has failed and I want to redesign and rewind the stator winding for 440 V operation. My reasoning is that the old arrangement, you would be seeing lot of harmonics (440 V VFD delivering 220 V). With the new voltage of 440 V, the output will see much less harmonics.

Do you, drive experts, see any problem with this idea ? I somehow got a nagging feeling about V/Hz issue but just could not pinpoint it.

 
Replies continue below

Recommended for you

If you are not needing to run in Open Loop Vector mode, you may not even need to have the drive tuned to the motor at all.

It's been a while since I programmed an ATV71, but I still have my manuals etc. I'll check to see if they show any details.
 
Jeff,

The client wants to run the motor at 160 RPM with the 415 V, 300 RPM winding (since the voltage is maxed out at 415 V for 150 RPM connection, he cannot go up to 160 RPM).

He also would like to have more torque at 160 RPM (it is a sort of vertical turning lathe). Can I advise him to increase the V/Hz from 415/50 to 440/60 so that he can get a higher voltage and torque at 160 RPM ?

* I would go green if only I were not yellow *
 