Greetings,
I am working on a project now as a design reviewer on the steel vendor, and we are clashing/fighting on two points in the serviceability checks as follow:
1-deflection
The vendor reference in the check of deflection is as per IBC2015 notes under table 1604.3 stating that "For secondary roof structural members supporting formed metal roofing, the live load deflection shall not exceed l/150" and I think the vendor reference is only for the purlin which can be secondary cold formed section but not for the main girder or rafter.
My reference regarding to deflection is table 1604.3 (roof Supporting non-plaster ceiling) L/240 LL and L/120 for DL+LL.
2-Drift (horizontal displacement)
The vendor guideline in the check of drift is as per AISC-2016-steel design guide#3 "Serviceability design considerations for steel buildings" table in page-30 the drift Serviceability considerations for cladding is(H/100) which is corresponding to the case that the cladding is supported by foundation.
but in the same table if we consider that cladding is supported by columns the value will be (H/500) which is matching with project case, moreover as per ASCE7-10 section#CC.1.2 "Drift of Walls and Frames" stating that: "Drifts (lateral deflections) of concern in serviceability checking arise primarily from the effects of wind. Drift limits in common usage for building design are on the order of 1/600 to 1/400 of the building"
I will appreciate your prompt advice and help on these two points
also see the attached of the screenshots from the codes references
Thank you
I am working on a project now as a design reviewer on the steel vendor, and we are clashing/fighting on two points in the serviceability checks as follow:
1-deflection
The vendor reference in the check of deflection is as per IBC2015 notes under table 1604.3 stating that "For secondary roof structural members supporting formed metal roofing, the live load deflection shall not exceed l/150" and I think the vendor reference is only for the purlin which can be secondary cold formed section but not for the main girder or rafter.
My reference regarding to deflection is table 1604.3 (roof Supporting non-plaster ceiling) L/240 LL and L/120 for DL+LL.
2-Drift (horizontal displacement)
The vendor guideline in the check of drift is as per AISC-2016-steel design guide#3 "Serviceability design considerations for steel buildings" table in page-30 the drift Serviceability considerations for cladding is(H/100) which is corresponding to the case that the cladding is supported by foundation.
but in the same table if we consider that cladding is supported by columns the value will be (H/500) which is matching with project case, moreover as per ASCE7-10 section#CC.1.2 "Drift of Walls and Frames" stating that: "Drifts (lateral deflections) of concern in serviceability checking arise primarily from the effects of wind. Drift limits in common usage for building design are on the order of 1/600 to 1/400 of the building"
I will appreciate your prompt advice and help on these two points
also see the attached of the screenshots from the codes references
Thank you