nivoo_boss
Structural
- Jul 15, 2021
- 132
Hey everyone!
So I'm designing a little extension of a shopping mall. It is to be made in steel. The mall itself is built in the 1970s in the Soviet era. I have the old drawings so I have a pretty good idea about the existing structures.
Anyway, I would like to support a new steel beam on a pre-existing RC beam. I would use chemical anchors to fasten the support part to the end of the RC beam. The design shear force on four anchors is around 61 kN. I'm using Hilti Profis software to design it and because of concrete edge breakout the anchor capacity is used around 300%. Now the thing is, in reality all the anchors are placed between the tightly spaced stirrups and longitudinal reinforcement - what concrete edge breakout could realistically happen here? Attached is a little drawing about the situation.
So I'm designing a little extension of a shopping mall. It is to be made in steel. The mall itself is built in the 1970s in the Soviet era. I have the old drawings so I have a pretty good idea about the existing structures.
Anyway, I would like to support a new steel beam on a pre-existing RC beam. I would use chemical anchors to fasten the support part to the end of the RC beam. The design shear force on four anchors is around 61 kN. I'm using Hilti Profis software to design it and because of concrete edge breakout the anchor capacity is used around 300%. Now the thing is, in reality all the anchors are placed between the tightly spaced stirrups and longitudinal reinforcement - what concrete edge breakout could realistically happen here? Attached is a little drawing about the situation.