A quick question about calculating the chemical availability. How would you know that you are pumping the required dosage for a pump that is not connected to the DCS?
The only way I can think of is to do the pump performance test (1-min test) every day. Or, less preferably to me, do a chemical residual test every day.
Any other ideas?

Regards,
A
 
Replies continue below

Recommended for you

Chemical metering pumps or dosing pumps are used for your type of application. These are generally diaphragm pumps that deliver a manually adjustable, but very consistent, volume per stroke. Counting strokes gives total volume.
 
Are regular samples taken of the process fluid to track chemistry? I would expect, if nothing else, your samples would readily indicate if your pump was degraded or malfunctioning. Also agreed with tracking chemical volume in the feed container - which I also assume takes place so that you know when to swap it out or refill it.
 