All, had a sprinkler contractor tell me that he designed a sprinkler system per the 'Chicago Fire Code'. The protected warehouse, had multiple row racks, 16-ft. deep with storage of Class I and III commodities to a height of 30-ft. with a ceiling height of 40-ft. Ceiling protection only with a design density of 0.25/2500. This protection per the NFPA 13 standard is not sufficient. this system should have been an ESFR system. Why would a fire protection contractor knowingly install a system that is not designed correctly to the current standard of NFPA 13? This is unethical, unprofessional and morally wrong. I could not sleep at night if I knew I designed a system that would not properly protect a building. I did look up the 'Chicago Fire Code' and there is language that was apparently used in the 1970's or earlier that I have never seen. The Chicago Code indicates that freight warehouses with 14-ft. high storage be protected by a MINIMUM design of 0.25/2500. Wouldn't the designer know this is a minimum and not the proper design? I think this is unbelievable. My question is this, what recourse does the building owner have? I would think the building owner could sue the general contractor and the sprinkler contractor but how likely would it be to win a lawsuit in these type of cases? Thanks in advance, JC