I am troubleshooting a job where chillers were just replaced. As the building load satisfies and control valves close, the chillers are going off on low-flow. I suspect that I know why, but I wanted to run something past everyone.
A rough drawing of the system is attached. It is a very poor design that has been that way since the mid 80's. They have 2 chillers, 2 primary pumps, and 5 AHU coils. They run both primary pumps and run water through both chillers all the time! Even when a chiller is not running, they pump water through it. So right there, they are blending and losing temperature. Then, they are blending again at the coils.
Each coil has a tertiary pump that constantly recirculates the coil. Depending on the position of the 2-way control valves, the coils are either 100% recirculating or blending water to some degree. So the water that actually hits the coil is much warmer than what is being produced by the chiller most of the time. Lots of improvements could be made for sure.
All that aside, I have a specific question about flow. All pumps are constant volume, but the overall system is really a variable-primary system. As 2-way control valves close, the flow in the primary system begins to drop. There are AUTOFLOW valves just upstream of the 2-way valves. I have attached a cut sheet, but I have had no luck researching these valves. I'm not sure what they are, but I think they are pressure-independent valves that attempt to pass a fixed GPM at all times. So these valves are always bypassing water to guarantee a minimum flow back to the chillers.
I think this concept "worked" with the old chillers, but the new ones probably have a more sensitive low-flow limit, which is knocking them offline as the loads get satisfied. So finally my question:
Since the coils pump continues to run, even when the 2-way valve is closed, couldn't that pumps cause the pressure at P2 to be higher than P1? I understand the bypass line with the check valve directs flow back to the suction of the coil pump, but couldn't the P2 pressure still be above P1? If so, then there would not be primary flow returning to the chillers through the AUTOFLOW valves.
Thanks for you help
A rough drawing of the system is attached. It is a very poor design that has been that way since the mid 80's. They have 2 chillers, 2 primary pumps, and 5 AHU coils. They run both primary pumps and run water through both chillers all the time! Even when a chiller is not running, they pump water through it. So right there, they are blending and losing temperature. Then, they are blending again at the coils.
Each coil has a tertiary pump that constantly recirculates the coil. Depending on the position of the 2-way control valves, the coils are either 100% recirculating or blending water to some degree. So the water that actually hits the coil is much warmer than what is being produced by the chiller most of the time. Lots of improvements could be made for sure.
All that aside, I have a specific question about flow. All pumps are constant volume, but the overall system is really a variable-primary system. As 2-way control valves close, the flow in the primary system begins to drop. There are AUTOFLOW valves just upstream of the 2-way valves. I have attached a cut sheet, but I have had no luck researching these valves. I'm not sure what they are, but I think they are pressure-independent valves that attempt to pass a fixed GPM at all times. So these valves are always bypassing water to guarantee a minimum flow back to the chillers.
I think this concept "worked" with the old chillers, but the new ones probably have a more sensitive low-flow limit, which is knocking them offline as the loads get satisfied. So finally my question:
Since the coils pump continues to run, even when the 2-way valve is closed, couldn't that pumps cause the pressure at P2 to be higher than P1? I understand the bypass line with the check valve directs flow back to the suction of the coil pump, but couldn't the P2 pressure still be above P1? If so, then there would not be primary flow returning to the chillers through the AUTOFLOW valves.
Thanks for you help