Ive been tasked to find some sort of commercial pre-built support/stand system for chilled water pipe that has some sort of thermal break. Any one have any suggestions.

If nothing like that is out there what ideas do you have or do you use.

Right now a lot of are stands have been welded to the pipe then some insulation run down the stand 20-26 inches. My boss wants something better to isolate the stand from the pipe.

Thanks in advanced.
 
Replies continue below

Recommended for you

I did a little checking on our extensive chilled water system. They essentially used two thermal break materials, Transite or cork depending on the loads. The pipe insulation is cork or Foamglas. Most of the larger pipe is held in hangers and the hanger is partially insulated as you describe. We also have a lot of external hangers.

Our Traniste was the old style, cement/asbestos.

Info on foam glass

 
Inside-building type environment or outside? Large-bore chilled water piping or small? Would plastic support columns be feasible?
 
its inside but exposed to outside air 4",6" and 8" pipe. Plastic may be an option in some areas good suggestion thanks
 