chilled water pipework expansion loop

Status
Not open for further replies.

funnyguy

Mechanical
Sep 16, 2003
4
Dear all,
I would like to know, when to use expansion loop for chilled water pipework??

thank you very much
 
Replies continue below

Recommended for you

There are three factors you need to consider.

1. What material is the pipe constructed from.

2. What is the operating temperature difference.

3. What is the length of the pipe.

For example, a mild steel pipe containing chilled water with an operating teperature difference of 25 K and a pipe length of 75 m gives,

coeff. of expansion of mild steel @ 25 K delta T = 0.284 mm/m

expansion of pipe is (0.284 x 75) = 21.3 mm

I hope this helps.
 