Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Chilled water piping calculations

Status
Not open for further replies.

tikitime

Mechanical
Apr 9, 2002
23
When you are sizing your chilled water piping and pump, do you typically include the pressure drop for such items as the suction diffuser, flex connections, air separator, etc. or are you mainly concerned with the coil, fittings, valves and such? In all the examples I've seen, only the main components were included.

Thanks for your help!
 
Replies continue below

Recommended for you

You include all of them plus some more for safety and for future expansion. You also put in aging allowance for piping friction loss about equal to 15% for closed systems. About 60% for open systems. Also for open systems you must add the static head hight of the liquid highest level above the level of the water in the suction.
You select the pump with the capability of going to a larger impeller in the future. You select the pump motor hp such that the motor will not be overloaded as the pump ride its pump curve. If you specify a pump with inadequate capacity you will be responsible to have it removed & replace with one that works!
 