Dear sirs:

I've been estimating chilled water cooling coil "delta P", finding very diffferent values among common manufacturers ( DataAire (45 ft H2O), Liebert (10 ft), , APC(20 ft). for the similar equipment


Do you have a rough or practical standard value?

Regards,

schola
 
Replies continue below

Recommended for you

The above replies are noraml ranges of DP. But the DP can be different depending on the Cv and the flow rate. You can use the : Q= Cv sqrt(DP) equation to calculate any DP and flow rate Q, if you know the Cv of the equipment.

Remember, the higher the DP, the higher you have to pay in energy for pumping the fluid through the equipment.
regards,
 