Has anyone done a chiller efficiency test. We are getting some weird numbers. Heat balance is supposed to be 5% or less. We are getting 30% to 40%. The machines are running well, tubes have been cleaned. They are carrier low pressure 540 ton. These are my readings I took at this moment:
ref temp: 41
chw sup temp: 44
ret chw temp: 56
cond ref temp: 97
cond wat temp out: 91
ent cond wat temp: 83
capacity: 101%
suction: -16
discharge:7
The main difference from design spec is the condenser delta T which was 14 but now reads around 7 to 8 psi most of the time. Could this be the prob?
We cut back on condenser water flow to it's design spec of 3.4 psi differential. It was at 6psi.
Any ideas?