Hi,
We've run into an issue where the chiller we bought is rated at 5kA SCCR and the available short circuit current at the switch gear is 52kA. The manufacturer says there isn't anything they can do to change the rating, we can't modify it ourselves without losing our warranty, and the breakers they used do not have a any tested series rating available.
I attached the chiller schematic along with the part numbers for the electrical components for reference.
One option we are considering is specifying a 480V-480V transformer with a custom impedance to limit the fault current down to 5kA. We're thinking of specifying a 320KVA transformer with an impedance of 7.7%. Using the MVA method I get a 77% voltage drop at the chiller during starting. Anything I am not considering or should be aware of?
The specs for the chiller are as follows,
460V
MCA = 383.9
ICF = 1380.6
Thanks,
CanisLupus
We've run into an issue where the chiller we bought is rated at 5kA SCCR and the available short circuit current at the switch gear is 52kA. The manufacturer says there isn't anything they can do to change the rating, we can't modify it ourselves without losing our warranty, and the breakers they used do not have a any tested series rating available.
I attached the chiller schematic along with the part numbers for the electrical components for reference.
One option we are considering is specifying a 480V-480V transformer with a custom impedance to limit the fault current down to 5kA. We're thinking of specifying a 320KVA transformer with an impedance of 7.7%. Using the MVA method I get a 77% voltage drop at the chiller during starting. Anything I am not considering or should be aware of?
The specs for the chiller are as follows,
460V
MCA = 383.9
ICF = 1380.6
Thanks,
CanisLupus