I hope everyone had a nice weekend. I haven't had to do a motor cable specification in quite some time, so just looking to make sure I am not to rusty.
I have a Chiller motor with an FLA of 1045 amps and a MCA of 1306.
Because the MCA is 1306 amps, I will have to provide wire for at least 1306 amps. So in this particular case, 3 sets of 600s would not be acceptable and we would have to go to 4 sets of 400s minimum.
My question is what size breaker can be utilized on this equipment? Is it allowable to use a 1200 amp breaker with 1200 amp class L fuses (or other appropriate fuse class for the equipment we are feeding?) The chiller is VSD driven so inrush current is limited to the maximum FLA, so inrush is not a concern. The 1200 amp fuse curves are also fine for continued operation at the 1045 amp design power consumption.
More generally stated: "Is there a requirement that the breaker size is larger than the MCA determined cable size by any certain margin?" I don't believe so, but just want to double-check that I am not missing anything from a code compliance perspective.
This is all 60hz, 460V power.
Thanks
Rob
I hope everyone had a nice weekend. I haven't had to do a motor cable specification in quite some time, so just looking to make sure I am not to rusty.
I have a Chiller motor with an FLA of 1045 amps and a MCA of 1306.
Because the MCA is 1306 amps, I will have to provide wire for at least 1306 amps. So in this particular case, 3 sets of 600s would not be acceptable and we would have to go to 4 sets of 400s minimum.
My question is what size breaker can be utilized on this equipment? Is it allowable to use a 1200 amp breaker with 1200 amp class L fuses (or other appropriate fuse class for the equipment we are feeding?) The chiller is VSD driven so inrush current is limited to the maximum FLA, so inrush is not a concern. The 1200 amp fuse curves are also fine for continued operation at the 1045 amp design power consumption.
More generally stated: "Is there a requirement that the breaker size is larger than the MCA determined cable size by any certain margin?" I don't believe so, but just want to double-check that I am not missing anything from a code compliance perspective.
This is all 60hz, 460V power.
Thanks
Rob