Anyone is familiar with chillers power consumption?

I see in a technical data sheet that a 155 tons air-cooled chiller made by Trane requires a 310 amps disconnect switch (@575V).

But I saw elsewhere on the net that "One ton of cooling is the amount of heat absorbed by one ton of ice melting in one day: 12,000 Btu/h or 3.516 thermal kilowatts (kW)."

So I would suppose that the 155 tons chiller uses 550 kW of power. That would mean more than 500 amps @ 575V, which is a little over the 310 amps requirement... Where is my mistake?
 
Replies continue below

Recommended for you

The chiller is using its input energy to move heat, not to produce heat (or its absence). Therefore it is possible to make a simple power comparison and get an apparent efficiency greater than 100%, but only because it is watts of power used to move watts of heat.
 
Right on davidbeach!

You need the COP - Coefficient Of Performance, for a better approximation. They often range from 1.7 to 3.5 or there-abouts. This is the efficiency at which the system "moves heat". This means your Power estimate would be divided by the COP. A lot lower!

Keith Cress
Flamin Systems, Inc.- <
 