My questions are: How do I know if the contactors used in the motor starter is properly matched to the load? Could an under-rated contactor aggravate the situation of voltage imbalance at the contactor terminals thereby causing yet higher current imbalance to the motor?
Let me explain:
A customer reported recurring occasional and failure to start of it's chillers due to "current imbalance." The set point for current imbalance is 15%. At 1.1% utility voltage imbalance, this current imbalance setpoint is reached thus tripping the chiller.
When they run the chiller on in-house generators with 0.5% voltage unbalance, no tripping occurrs. There was current imbalance of 3.5% which will not trip the chillers.
Utility voltage however, is allowed by the Regulatory body to vary up to 2.5% maximum at the point of common coupling (metering point) in which case the previous 1.1% is still within allowable range.
The latest event was that, even at utility voltage unbalance of only 0.4% the chillers already tripped. Voltage unbalance at the motor terminals was not known.
My intial survey of the site revealed that the motors are Y-Delta started with rated line Amps of 708A, at 380Volts, 60Hz. this would make the each of the two delta contactor (running) carry a full load of 708A/1.732 or 408Amps.
The delta contactors have this rating:
AC-1: 1000V, 500A
AC-3: V 240 400 415
kW 187 312 324
by ratio, kW at 380V= 296.4kW
I have read before that AC-3 should be considered for inductive load such as this motor but how do I make the comparison since the AC-3 ratings are in kW? Is this contactor under-rated?
I suspect that the contactors might not be under-rated, but I am not sure. But one of them had stuck relay contacts as of the latest event causing the upstream breaker to trip. I might be barking up the wrong tree here as far as the contactors are concerned but could an under-rated contactor aggravate the current imbalance condition?
Please give your comments. I would appreciate your thoughts about this.
Thanks.
My questions are: How do I know if the contactors used in the motor starter is properly matched to the load? Could an under-rated contactor aggravate the situation of voltage imbalance at the contactor terminals thereby causing yet higher current imbalance to the motor?
Let me explain:
A customer reported recurring occasional and failure to start of it's chillers due to "current imbalance." The set point for current imbalance is 15%. At 1.1% utility voltage imbalance, this current imbalance setpoint is reached thus tripping the chiller.
When they run the chiller on in-house generators with 0.5% voltage unbalance, no tripping occurrs. There was current imbalance of 3.5% which will not trip the chillers.
Utility voltage however, is allowed by the Regulatory body to vary up to 2.5% maximum at the point of common coupling (metering point) in which case the previous 1.1% is still within allowable range.
The latest event was that, even at utility voltage unbalance of only 0.4% the chillers already tripped. Voltage unbalance at the motor terminals was not known.
My intial survey of the site revealed that the motors are Y-Delta started with rated line Amps of 708A, at 380Volts, 60Hz. this would make the each of the two delta contactor (running) carry a full load of 708A/1.732 or 408Amps.
The delta contactors have this rating:
AC-1: 1000V, 500A
AC-3: V 240 400 415
kW 187 312 324
by ratio, kW at 380V= 296.4kW
I have read before that AC-3 should be considered for inductive load such as this motor but how do I make the comparison since the AC-3 ratings are in kW? Is this contactor under-rated?
I suspect that the contactors might not be under-rated, but I am not sure. But one of them had stuck relay contacts as of the latest event causing the upstream breaker to trip. I might be barking up the wrong tree here as far as the contactors are concerned but could an under-rated contactor aggravate the current imbalance condition?
Please give your comments. I would appreciate your thoughts about this.