Cinema Fire protection

Status
Not open for further replies.

amrzaghlol

Mechanical
May 3, 2016
1
i am designing a fire fighting system for a mall which contain a cinema in two floors
so where i can find a guide lines for cinema protection
cause i have searched but i don't found something specific
 
Replies continue below

Recommended for you

Occupancy classification of Cinema comes under Assembly group (A2) as per International building code. You must follow International building code chapter 3 for occupancy classification and chapter 9 for requirement of sprinkler and standpipe systems.
 
In the USA, also check NFPA 101 for occupancy classification since Fire Marshals and Insurance companies use NFPA's as their guidelines.
 