Circuit Beaker - Switch Disconnector (Rated Current Selection Method) 1

Status
Not open for further replies.

luiscunha1978

Mechanical
Feb 8, 2019
21
Hello,

First sorry for my ignorance, but I really need help to understand an issue related to an electrical installation design that I have seen recently.

I have an installation with several electrical boards: the Main Distribution Board and Secondary Distribution Boards powered from the first one.

The output of the Main Distribution Board and which will supply the Secondary Distribution Board is made with a 3P 125A MCB (Q1) and through a 3x50+1x25mm2 cable. This cable between the the boards is protected against overloads and short-circuits by the mentioned circuit breaker.

At the arrival of the Secondary Distribution Board I have a 160A 4P Switch Disconnector (S1) and in this Board diagram the maximum load current of the busbar is also 160A.

Please see the below image for a better understandig:

Image2_oiorpc.png


1) What is the criterion for choosing the Switch Disconnector (S1) rated current [In], since the Circuit Breaker (Q1) upstream rated current is 125A.
2) Are there circuit-breaker/switch-disconnector coordination tables to determine the current selectivity between these two type of devices?
3) The busbar rated current of the Secondary Distribution Board could be greater than the S1 rated current [In]?
4) From my poor understanding the Switch Disconnector is a control device that can be used to open and close a circuit under normal operating conditions. Thus, the Switch Disconnector can make and break its rated current. For an overload or a short-circuit, it must be protected by an upstream device In this particualr situation that protection must be assure by the Q1 Circuit Breaker installed in the Main Distribution Board. Am I Correct? If so, in this particular situaion the S1 is protected by the Q1?

Thank you in advanced,
Luis
 
Replies continue below

Recommended for you

Your understanding is correct, S1 as well as the busbars in secondary DB are protected by Q1.
Q1 also protects the cable between the two boards and also acts as back up to the outgoing feeder protection at Secondary DB.
 
The S1 device has no protective functionality, it is simply a switch. There is no "coordination" of trip values because there is no trip function of S1. It must simply be rated to disconnect the current of the protective device ahead of it, in this case the 125A MCB Q1. The fact that it is larger is immaterial, most likely because with no trip functionality, the switching device is simply rated for the maximum capability of the frame rating, in this case 160A. The same would likely be true of the bus bars. Both elements COULD be rated for 125A, but what is actually made and available is 160A.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 