Hello Everyone,
We have panel board used for commercial purpose with 100A 3Phase 440V main breaker Model GE TCD134100WL, size of main feeder is 30mm2 THHN.
Loads: Lighting and Outlet, Aircon, CCTV.
Power Supply : 440V, 3Phase, 4Wire
No voltage imbalance.230V single phase load used line to neutral.
During full operation, we measured a phase current of 50-65A and the main breaker becomes hot. I doubt if the breaker is overloaded if we only use 65% of its capacity?
The main feeder also getting warmer and it is rated at 115A.
We also measure 6A at neutral conductor (also 30mm2 THHN).
Any thoughts?
Thank you in advance.