Hello everyone:
We have a 3MW 5.5kV DOL - started motor installed in a concrete plant. The process designer says that it may be started and stopped several times a day. So contactor shall be used to start and stop it. However, the client requires that vacuum circuit breaker will be used to protect the feeder circuit rated 1.5MW and above. Therefore, both circuit breaker and contactor ( without fuse) will be used on the feeder. Generally we use only one of them, CB or fused contactor, not both. Does somebody use this configuration on previous project? I wonder whether any manufacturer will provide such kind of switchgear? Is there any special protection consideration on this group of CB and contactor ?
Thanks,
Parkpower
We have a 3MW 5.5kV DOL - started motor installed in a concrete plant. The process designer says that it may be started and stopped several times a day. So contactor shall be used to start and stop it. However, the client requires that vacuum circuit breaker will be used to protect the feeder circuit rated 1.5MW and above. Therefore, both circuit breaker and contactor ( without fuse) will be used on the feeder. Generally we use only one of them, CB or fused contactor, not both. Does somebody use this configuration on previous project? I wonder whether any manufacturer will provide such kind of switchgear? Is there any special protection consideration on this group of CB and contactor ?