Distribution73
Electrical
- Mar 18, 2015
- 39
Hello,
I can see that the standard duty cycle for circuit breakers is well documented and can be found for example on the breaker nameplate. However this standard rating appears to cover two closing operations. What is unclear to me is what happens when we reach the last "open" of the sequence. For example, if we have a breaker with a rated duty cycle "O-0.3s-CO-15s-CO" and we want to attempt an additional close (for example for a 3 shot reclosing scheme): Should we contact the manufacturer to see the minimum reclaim time? or Is this time between duty cycles standarized?
Thank you.
I can see that the standard duty cycle for circuit breakers is well documented and can be found for example on the breaker nameplate. However this standard rating appears to cover two closing operations. What is unclear to me is what happens when we reach the last "open" of the sequence. For example, if we have a breaker with a rated duty cycle "O-0.3s-CO-15s-CO" and we want to attempt an additional close (for example for a 3 shot reclosing scheme): Should we contact the manufacturer to see the minimum reclaim time? or Is this time between duty cycles standarized?