Suggestion to scud27 (Electrical) Oct 18, 2002 marked ///\\My opinion is that fuses are the most convenient and cheap way of protection also taking into account that they really limit the peak of current but...
///Agree up to but...\\I wouldn't say that a CB has a complex mechanism
///In terms of part count, it is definitely more complex than a fuse or even three fuses.\\ or, at least, a CB is structured in such a way that if it breaks it will open the 3 phases together - whether it is an thermal magnetic or an electronic based one.
///This has become somewhat less important with the advent of electronic or smart overloads. Therefore, the emphasis on the simultaneous opening of the three poles of the circuit breakers is becoming old fashined.\\ Also, remember that short circuit is not protected by the release but by a different phenomenon that is the reflex of the shaft. In real life, the contacts will open in 3 to 10 msecs all together since, even though only one phase feels the SC, they are mechanically connected.
Fuses have the bad idea to become old in different ways. This means that you might have a single fuse that bore more current than the others and wrecks, thus causing a bi-phase operation of teh motor and possibly burns it.
///Again, this reasoning is somewhat oldfashoned by the application of electronic or smart overload protective relays.\\ This is the real problem of fuses.
///Used to be, since the electronic or smart overload relay sense the singlephasing.\\By the way, each philosopy is right: when you need to protect an expensive motor, use fuses if you worry about short circuit and CB (maybe with a motor protection release) if you worry about overload and locked rotor.
And remember that, for really high currents, CBs are often cheaper than fuses...
///It may be. However, if the circuit breaker clears three short circuit faults, it loses the UL label and shall be replaced. How many places are really replacing the circuit breakers after three shorts? I have not seen many markups on circuit breakers indicating the it cleared one fault, two faults, etc. When it comes to fuses, the short may damage one fuse only if the electronic overload trips on singlephasing. Then, the fuse protection is not that expensive.\\\