A family member is (in my opinion) about to make a mess at minimum and a disaster possibly.
In an attempt to use wiring that is already in place to create a mobile home 50 amp 4 pole RV connection. He plans to use a series of different types and sizes of wire by splicing together conductors that are in place but unused to complete a 125 foot run. From the breaker there will be two 10 awg romex wires each one will have both insulated wires twisted together the two bare wires to ground. A 6awg will serve as the white. Common what ever it is called, this runs 15 feet into attic. in a box splice the "four leads" 2 10 awg hot,
2 10 awg hot, 2 10 bare ground, 6 awg white common ,, , to to four 8 awg ran in 1" conduit 40 feet. The last leg outside is back to 2 10 awg direct burial and 1 number 8 as common simular to first of run.
WHEN you finish laughing or scratching your head please help me to exlain(if I am correct) why this is a bad idea as he should know more about this than I. It just sounds like a potential disaster to me. but I can not explain why.
I have been reading. He says that two 10 awg twisted together should handle 50 amp RV CIRCUIT. I read it should be 6 awg. And elsewhere that it would take 3 10's or 2 10's and a 12 to equal 6 awg. Another site said 4 conductors of 6awg required for rv connection that is over 100feet. One site said 4 conductors of 4awg. For four pole RV hookup 125 foot run
In an attempt to use wiring that is already in place to create a mobile home 50 amp 4 pole RV connection. He plans to use a series of different types and sizes of wire by splicing together conductors that are in place but unused to complete a 125 foot run. From the breaker there will be two 10 awg romex wires each one will have both insulated wires twisted together the two bare wires to ground. A 6awg will serve as the white. Common what ever it is called, this runs 15 feet into attic. in a box splice the "four leads" 2 10 awg hot,
2 10 awg hot, 2 10 bare ground, 6 awg white common ,, , to to four 8 awg ran in 1" conduit 40 feet. The last leg outside is back to 2 10 awg direct burial and 1 number 8 as common simular to first of run.
WHEN you finish laughing or scratching your head please help me to exlain(if I am correct) why this is a bad idea as he should know more about this than I. It just sounds like a potential disaster to me. but I can not explain why.
I have been reading. He says that two 10 awg twisted together should handle 50 amp RV CIRCUIT. I read it should be 6 awg. And elsewhere that it would take 3 10's or 2 10's and a 12 to equal 6 awg. Another site said 4 conductors of 6awg required for rv connection that is over 100feet. One site said 4 conductors of 4awg. For four pole RV hookup 125 foot run