Hi everyone,
We have a problem with our circulation pump of the firewater tank. the rated power on the plate shows 11 kw,
while our reading given 4.7 kw (8.5 R-Y-B, V-L-L -396v) & (Pump 35 l/s & 15.4 m and suction lift of 1.6m, dH-0 m)
we have enhanced the suction discharge lines as 8 nos of foot valves (PN16)in the suction of 150mm and 12 nos MFP nozzles of 50mm connected in 100mm discharge line in order to cover the entire tank water for circulation.
Besides the flow reading was less as 21 l/s in fully opened line and the discharge pressure in the downstream was 6-7 psi.
NPSH available has been proven above the required to aforementioned design. ( NPSHa =3.9 m, NPSHr =2.1m )
Is the pump performing under and cause cavitation? could anyone diagnose the problem and advise me what is lacking
Please