sspeare
Mechanical
- Dec 25, 2004
- 96
DESCRIPTION OF CIRCUIT:
Elevator motor is 40 HP, 208 Volt/3-phase. Motor FLA from NEC Table is 114 Amps. Breaker sizing: 114 FLA x 2.5 = 285 Amps, round up to 300 Amp. Circuit Breaker #1 is in the Main Dist Panel "MDP". CB #1 is a 300 Amp thermal magnetic breaker, as follows: Siemens JD Frame, model number JXD63B300. CB #2 is inside the elevator machine room. CB #2 serves as the NEC-required disconnect and OCP device. CB #2 is enclosed, and is exactly the same rating and model as CB #1. The cable between CB #1 and CB #2 is copper: 3-#2/0 phase conductors with 1-#4 equipment ground.
THE PROBLEM:
What I'm hearing from the field is: "the breaker is tripping." I have not managed to find out which breaker, or if it's both breakers. The electrician says the instantaneous trips are factory-set at the minimum. The electrician is asking me "how high" to set the adjustable instantaneous trips for these 2 breakers in series. I'm telling him to check for faults first.
QUESTIONS:
1) Am I in trouble because these breakers in series are "fighting" each other with their instantaneous trips?
2) Should I replace the CB in the machine room with a fusible switch?
3) Assuming we can't locate a fault, what can be done?
Elevator motor is 40 HP, 208 Volt/3-phase. Motor FLA from NEC Table is 114 Amps. Breaker sizing: 114 FLA x 2.5 = 285 Amps, round up to 300 Amp. Circuit Breaker #1 is in the Main Dist Panel "MDP". CB #1 is a 300 Amp thermal magnetic breaker, as follows: Siemens JD Frame, model number JXD63B300. CB #2 is inside the elevator machine room. CB #2 serves as the NEC-required disconnect and OCP device. CB #2 is enclosed, and is exactly the same rating and model as CB #1. The cable between CB #1 and CB #2 is copper: 3-#2/0 phase conductors with 1-#4 equipment ground.
THE PROBLEM:
What I'm hearing from the field is: "the breaker is tripping." I have not managed to find out which breaker, or if it's both breakers. The electrician says the instantaneous trips are factory-set at the minimum. The electrician is asking me "how high" to set the adjustable instantaneous trips for these 2 breakers in series. I'm telling him to check for faults first.
QUESTIONS:
1) Am I in trouble because these breakers in series are "fighting" each other with their instantaneous trips?
2) Should I replace the CB in the machine room with a fusible switch?
3) Assuming we can't locate a fault, what can be done?