Hello,

I'm staring at a U-1 that reads:

Shell: SA-264 20% Type 316 S/S on SA-285-C Backing, Nominal thickness 3/8 in.

My question, is it:

a) 20% of the 3/8 is clad, with an overall thickness of 3/8

or

b) 3/8" CS plus 20% clad, so an overall of 0.450", 0.075" of which is stainless clad?

Edit: after speaking with a few colleagues I feel pretty confident that option a is correct, but I'd still like to get others' opinions.

Thanks
 
Replies continue below

Recommended for you

no way to tell...

The problem with sloppy work is that the supply FAR EXCEEDS the demand
 
Since only the backing is used in the pressure rating I would think that the dimension is strictly the backing, but from the wording there is no way to tell.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube
 
Section VIII Division 1 requires you to put list the uncorroded thicknesses on the U-1, and normally cladding and weld overlay are considered to act as the corrosion allowance, so the answer appears to be (a).

However, 80% of 3/8" is 0.300", which is not a standard plate thickness. You would have to pay a premium to get plate that's 0.300" thick, but for what purpose?

I think option (b) is more likely.