Hi all,
I took ASME Sec VIII PSV sizing courses ~5 years ago and remain familiar with API 520, 521, etc. but do not regularly perform PSV sizing exercises. I am hoping someone can clarify how to handle some simple failure scenarios. As I understand it, only one device failure must be accounted for per scenario unless multiple devices would fail due to the same event. In addition, it is my recollection that instrumentation/controls cannot be counted on to prevent a failure scenario.
Scenario 1 - Liquid
A centrifugal pump is controlled by a VFD to maintain a set discharge pressure. The liquid passes through a level control valve into a buffer tank. The only liquid overpressure scenario for this tank is that the LCV fails open. My questions for this scenario:
1. Does this scenario truly count as a failure, since the LCV is open under normal operation and is held in a partially open state by an I/P converter?
2. With the pump being on a VFD, do I have to consider flow conditions on the curve, or am I allowed to use normal operating conditions?
Scenarios 2/3 - Gas
Gas used to pressure the head space of the tank is regulated down to a pressure below the MAWP of the tank. When pressurization is required, the gas passes through a pressure control valve prior to entering the tank. The failure opportunities here are the regulator and the PCV.
1. Similar to the liquid scenario, does the PCV "failing" open truly count as a failure? I.e. if I'm examining a regulator failure, do I have to use the maximum C[sub]v[/sub] value of the PCV?
I took ASME Sec VIII PSV sizing courses ~5 years ago and remain familiar with API 520, 521, etc. but do not regularly perform PSV sizing exercises. I am hoping someone can clarify how to handle some simple failure scenarios. As I understand it, only one device failure must be accounted for per scenario unless multiple devices would fail due to the same event. In addition, it is my recollection that instrumentation/controls cannot be counted on to prevent a failure scenario.
Scenario 1 - Liquid
A centrifugal pump is controlled by a VFD to maintain a set discharge pressure. The liquid passes through a level control valve into a buffer tank. The only liquid overpressure scenario for this tank is that the LCV fails open. My questions for this scenario:
1. Does this scenario truly count as a failure, since the LCV is open under normal operation and is held in a partially open state by an I/P converter?
2. With the pump being on a VFD, do I have to consider flow conditions on the curve, or am I allowed to use normal operating conditions?
Scenarios 2/3 - Gas
Gas used to pressure the head space of the tank is regulated down to a pressure below the MAWP of the tank. When pressurization is required, the gas passes through a pressure control valve prior to entering the tank. The failure opportunities here are the regulator and the PCV.
1. Similar to the liquid scenario, does the PCV "failing" open truly count as a failure? I.e. if I'm examining a regulator failure, do I have to use the maximum C[sub]v[/sub] value of the PCV?