Clean Agent Nozzle spacing 1

Status
Not open for further replies.

newmind

Mechanical
Dec 1, 2008
16
What is usual spacing of clean agent nozzle with a standard orifice diameter?
 
Replies continue below

Recommended for you

not a clean agent expert but 1. have to hit concentration 2. install per manufacture

if you are thinking spacing criteria like for sprinkler heads, have never seen that.
 
Spacing shall be in accordance with its listing.
 
Nozzle spacing is based on calculations performed by the manufacturer's software. There is not a standard (like 13) that can be used for clean agent. You must meet concentration and discharge distances when designing.

There is not any "standard" oriface diameters that I am aware of.
 
Thanks for suggestions guys, does anyone has a flow calculation software that can be shared to me?
 
Check NFPA 2001 and the nozzle listing data. Your lack of design information limits our ability to help you.
 
There is no standard orifice for clean agent nozzles. They are sized according to the calculation program specific to that agent. The basic nozzle size matches the pipe size as determined by the program and the orifice sizes are custom drilled to meet the calculation results.

As mentioned previously the number of nozzles is determined by the listed coverage per nozzle. What you have to watch though is areas with suspended ceilings. If the coverage is ok with one nozzle you may very easily "overpressurize" the area in the vicinity of the nozzle and blow out tiles. To retain ceiling tile in place, and thus retain the agent, you generally have to spread out the discharge to more nozzles. I don't think the manufacturer design manuals tell you this.
 
KCfpe is correct except I might add that a room has to pass 'room integrity testing'. Ceiling tiles coming out is not an option and they must be pinned in place. A system isn't designed to compensate for tiles blowing out.

Regards
Dave
 
I appreciated all the tips and suggestions. I will ask my friends ,If they can lend NFPA 2001 book.
 