Uner B31.3, would clean steam tubing, orbitally welded, 60 psig require X-ray testing? As I understand it, Category D service fluids don't require X-ray testing.
Clean steam service meets the design pressure and temperature (-20F to 366F) requirements for Category D. It also meets the nonflammable and nontoxic requirements for Category D.
The only requirement it might not meet is tne "not damaging to human tissues as defined in para 300.2" requirement. I'm not sure how to interpret this since it seems as if any fluid at 365F would be "damaging to human tissue" yet a fluid at 365F would fall under the Category D definition.
Clean steam service meets the design pressure and temperature (-20F to 366F) requirements for Category D. It also meets the nonflammable and nontoxic requirements for Category D.
The only requirement it might not meet is tne "not damaging to human tissues as defined in para 300.2" requirement. I'm not sure how to interpret this since it seems as if any fluid at 365F would be "damaging to human tissue" yet a fluid at 365F would fall under the Category D definition.