Marko04
Industrial
- Apr 13, 2016
- 7
Hi,
I am currently in process of designing a clip with a thermal break for attaching the cladding on to. The clip is suppose to handle a dead load of 90 lbs. The clip's body consists of 6063 T5 aluminum alloy and
the thermal break is Polyamide. The clip is 5 inches long. Since aluminum has a greater tensile strength than the polyamide strut, the critical factor in in this analysis was to see whether the bending stresses caused by the vertical acting load of 90lbs acting at a distance of 5 inches away from the fulcrum would cause the polyamide strut to deform. A safety factor of 1.7 was used in this analysis.
After viewing the results of the analysis ( looking at the Von Mises Stress chart and corresponding stress colors found in the model), I noticed some small "hot spot" areas that only appeared
on surface of the polyamide strut indicating stresses higher than polyamide's tensile strength. ( Please see the attached images). I am not sure how to interpret these results. Could these hot spot localized
higher than yield stresses be neglected and that the overall design is safe? I would assume that if these higher than yield stresses went through the whole thickness of the material that the design would then
not be safe, however, since these localized stresses appear only on surface of the polyamide strut could they be neglected and design deemed safe?
NOTE: The areas in red indicate stresses higher than yield
I am currently in process of designing a clip with a thermal break for attaching the cladding on to. The clip is suppose to handle a dead load of 90 lbs. The clip's body consists of 6063 T5 aluminum alloy and
the thermal break is Polyamide. The clip is 5 inches long. Since aluminum has a greater tensile strength than the polyamide strut, the critical factor in in this analysis was to see whether the bending stresses caused by the vertical acting load of 90lbs acting at a distance of 5 inches away from the fulcrum would cause the polyamide strut to deform. A safety factor of 1.7 was used in this analysis.
After viewing the results of the analysis ( looking at the Von Mises Stress chart and corresponding stress colors found in the model), I noticed some small "hot spot" areas that only appeared
on surface of the polyamide strut indicating stresses higher than polyamide's tensile strength. ( Please see the attached images). I am not sure how to interpret these results. Could these hot spot localized
higher than yield stresses be neglected and that the overall design is safe? I would assume that if these higher than yield stresses went through the whole thickness of the material that the design would then
not be safe, however, since these localized stresses appear only on surface of the polyamide strut could they be neglected and design deemed safe?
NOTE: The areas in red indicate stresses higher than yield