RustyPipez
Mechanical
- Dec 29, 2016
- 3
Hi all.
I have a glycol system that includes 3 air-cooled chillers with 3 pumps on a loop. The pumps are controlled by VFD's controlling pump speed using differential pressure. Off the loop are various fan coil units. I run minimum one chiller and one pump around the clock, adding chillers and pumps for seasonal changes in load.
In the past, I would have 575 GPM at 75% speed on the pump, with a differential pressure of 24 psi. The flow and pump speed were very stable since my load is pretty stable. Suddenly, with no changes to the system, my flow was greatly reduced, varying between 250-400 GPM with the same DP. The load has not changed, and doesn't change other than slight changes due to seasonal temperature differences. If I change my DP setpoint to 33 psi,the pump will speed up, and I can get flow in the range of 330-470, but the pump speed is now varying between 83%-90%. The reduced flow is also causing my return glycol temp to increase.
In it's present conditions, I need to run the pump at 100% to get the 575 GPM flow I had, but then the pressures are much higher than they should be.
This situation is the same regardless which chiller/pump combination I use.
My question is, Does this sound like a possible restriction in the loop? Or am I barking up the wrong tree?
Thanks for any assistance,
I have a glycol system that includes 3 air-cooled chillers with 3 pumps on a loop. The pumps are controlled by VFD's controlling pump speed using differential pressure. Off the loop are various fan coil units. I run minimum one chiller and one pump around the clock, adding chillers and pumps for seasonal changes in load.
In the past, I would have 575 GPM at 75% speed on the pump, with a differential pressure of 24 psi. The flow and pump speed were very stable since my load is pretty stable. Suddenly, with no changes to the system, my flow was greatly reduced, varying between 250-400 GPM with the same DP. The load has not changed, and doesn't change other than slight changes due to seasonal temperature differences. If I change my DP setpoint to 33 psi,the pump will speed up, and I can get flow in the range of 330-470, but the pump speed is now varying between 83%-90%. The reduced flow is also causing my return glycol temp to increase.
In it's present conditions, I need to run the pump at 100% to get the 575 GPM flow I had, but then the pressures are much higher than they should be.
This situation is the same regardless which chiller/pump combination I use.
My question is, Does this sound like a possible restriction in the loop? Or am I barking up the wrong tree?
Thanks for any assistance,