On a recent project, we’re infilling an opening in an exterior wall with CMU. The opening is 18’ tall, and the wall is running bond reinforced with #5 @ 24” o.c. We typically use stack bond for the majority of our projects because of architectural preference, so the spec called for truss reinforcing at 16” o.c. vertically plus a bond beam w/ 2#5 @ 12’-0” a.f.f. and at t/wall. There is no vertical load on the wall, it only needs to withstand wind pressure (basic wind speed of 90 mph). The mason did not install the bond beam at 12’-0” but installed the bond beam at the top of wall.
My first question is, if this is designed as a one way wall, other than the fact that the mason didn’t follow the documents, is there any other concern with a running bond masonry wall spanning 18 ft vertically with only truss type horizontal reinforcing? If so, is there a way to supplement the horizontal reinforcing without making them remove the top ~6 ft of wall and putting in a bond beam?
After reading a several other threads, I’m starting to wonder if my perception of the capability of running bond may be skewed by the fact that I’ve been typically using stack bond for a while, which makes me more cautious.
My first question is, if this is designed as a one way wall, other than the fact that the mason didn’t follow the documents, is there any other concern with a running bond masonry wall spanning 18 ft vertically with only truss type horizontal reinforcing? If so, is there a way to supplement the horizontal reinforcing without making them remove the top ~6 ft of wall and putting in a bond beam?
After reading a several other threads, I’m starting to wonder if my perception of the capability of running bond may be skewed by the fact that I’ve been typically using stack bond for a while, which makes me more cautious.