wvatecheng1
Structural
- Apr 28, 2009
- 4
About 2 years I designed a one-story 16ft tall middle school addition with 8" load-bearing walls and roof composed of vulcraft joists (@6 ft on center) spanning between 8' and 20' + 1.5" metal roof deck . The CMU walls are reinforced with #5@32" and #5 rebar at window and door jambs and headers. All the headers have bond beams with 2#5's. Also, control joints are located at 40-ft O.C.
No additional rebar was called out at the window sills.
Having said this, hairline cracks are developing in the CMU walls at several of the window sill locations, and at the headers of some of the double doors. We have total of 4 cracks on this 30,000-SF addition (about 3,000 LF of walls), but they occur in some of the most visible locations.
The owner is concerned that these cracks could somehow compromise the intergrity of the building.
Question: How do I go about re-assuring the owner that the building is safe and the cracks are cosmetic, without seeming dimissive??
No additional rebar was called out at the window sills.
Having said this, hairline cracks are developing in the CMU walls at several of the window sill locations, and at the headers of some of the double doors. We have total of 4 cracks on this 30,000-SF addition (about 3,000 LF of walls), but they occur in some of the most visible locations.
The owner is concerned that these cracks could somehow compromise the intergrity of the building.
Question: How do I go about re-assuring the owner that the building is safe and the cracks are cosmetic, without seeming dimissive??