ghostbuster7
Electrical
- Jun 25, 2007
- 80
The customer has a 10 MW. generator(4160 volt) wye connected to a wye-wye (27.6 kv.) step-up tx.There is no neutral wiring between generator and tx.The wyes at the tx. are solidly grounded and the wye at the generator is grounded thru a .4 ohm reactor.
There is no power to the high side of the tx.Turning on the generator,the reactor instantly blew and over 300 amps of current was recorded going thru this reactor.
The customer has been told to simply float the grounds either at the geny or tx. end and this will remove this ground current component.
With this proposed new set-up,I am concerned about voltage stability,generator warranties and system phase to ground faults.Any comments?
There is no power to the high side of the tx.Turning on the generator,the reactor instantly blew and over 300 amps of current was recorded going thru this reactor.
The customer has been told to simply float the grounds either at the geny or tx. end and this will remove this ground current component.
With this proposed new set-up,I am concerned about voltage stability,generator warranties and system phase to ground faults.Any comments?